Kohler Electric Generator Oncue issues
bdegnan
Newbie

I have Verizon FIOS (TV, Internet) with an Actiontec router.  I also have an Kohler generator with Oncue software.  Oncue allows remote access to monitor and control the generator. Oncue is an application that runs on a PC.

The issue I am having is the generator seems to be able to send emails (i.e. outbound) but Oncue cannot connect to the generator.  This is despite the fact that the generator passes the router connectivity test.  Oncue is also able to connect to the Kohler Oncue server.  It seems like the router will not allow an inbound connection to the generator's controller.  This is the case with software firewall (McAfee) turned off and Actiontec security set to lowest setting.  Required ports are forwarded properly.  Verizon tech guy confirmed this.

Kohler says the issue is the Actiontec router and that other Kohler customers have resolved the issue by replacing the router with a Netgear router.  This requires the other router to be in front of the Actiontec I believe.

I am looking for someone that has FIOS and a Kohler generator with Oncue who has gotten Oncue to work.  Any help would be greatly appreciated.

0 Likes
25 Replies
smith6612
Community Leader
Community Leader

Just out of curiosity, has the following been attempted to see if one of these helps with keeping the Generator on the network?

  • Assigning a Static IP / Using DHCP Reservation to reserve an IP for the Generator
  • Checking to see if for some reason, the generator's control unit is entering a funny power save mode due to a lack of communication, that isn't caused by connectivity to another router (Eg: the Comcast Gateway as pointed out above).

I didn't catch anything in this thread about whether the Generator was connected Wired or Wirelessly. Just to note some things, I've found with home automation appliances and also printers of all things, tend to cooperate on a Wired connection a lot better than they do on Wireless. Lots of software bugs I'm sure are to blame.

Second, here at home I use a Wi-FI connected thermostat. In the documentation, it is pointed out that the thermostat may not behave correctly if it does not have a Common Wire attached. Even though the unit will recharge it's battery and run off of the power supplied from the HVAC unit. If you don't connect a C Wire, the thermostat will still use Wi-Fi, but it will enter aggressive power saving modes to converse power. These aggressive power savings can cause the radio to only transmit periodically each second to maintain a session, but can cause the thermostat to respond to a ping in about 500ms. Additionally, the thermostat will POWER DOWN it's radio from time to time, especially as power runs low, and will connect to the network periodically to synchronize with a server on the Internet for weather data, temp data, and so on. WIth a C wire, the thermostat will keep the radio powered constantly and will not enter a power saving mode.

Third, the reason why I suggested a Static IP here, is in case the Generator happens to be doing something funny where it is releasing it's IP address due to a power saving setting, OR because the unit is having problems with IP address Conflicts, or in the case of the thermostat I use here at home, software bugs cause the thermostat to fail to renew it's IP address with DHCP. A Static IP can ensure no other device gets the IP that is otherwise being used by the generator, and overall makes troubleshooting a whole lot easier.

Just some food for thought.

EDIT: Glad to see the Static IP part was attempted. Good move. I'd keep it on Static/DHCP reservation for the sake of troubleshooting.

0 Likes
IronEdison
Newbie

I am a Kohler Certified Maintenance Technician, and have seen this problem before.

Here is the official solution, as detailed in the manual:  

1.6 Internet Configuration and
Security (Firewalls)
 
When using the OnCue PC application from a remote location behind a firewall, it may be necessary to configure the firewall to open port 808. 
 
The firewall may prompt you to allow OnCue to use port 808.   Contact your network administrator for assistance, if necessary.
 
When the generator set is connected to an intranet network behind a firewall, for example in a commercial or industrial setting, it may be necessary to configure the firewall to open port 5253 to permit an outbound connection. 
 
Contact your network administrator for assistance if necessary.
 
 
You can download the full manual for OnCue here:  http://ironedison.com/kohler-oncue
 
The manual is saved on the top right side of the page.
0 Likes
IronEdison
Newbie

I left out some important instructions on how to enable port forwarding.

Here is a link to the NetGear page that details how to enable port forwarding.    http://kb.netgear.com/app/answers/detail/a_id/24046  

If this link ever becomes disabled, just search "Port Forwarding" and the make / model of your router.  You can find the model of your router on a sticker on the bottom of the device.

Good Luck Everyone!

0 Likes
obmd1
Enthusiast - Level 2

I am working with a Kohler tech now to get oncue to even add the genset. He worked with the company and they were able to get in and remotely start it, so I know the connection is working... but the password generated by the machine is not recognized when I log in via the consumer side. could this still be a port issue? The IP address is issued, and server communicates...

0 Likes
Cynicalguy
Newbie

I just started having this issue when I upgrade my FIOS to 150/150 from 100/100.  I had to switch to the Quantum Router and get my internet via ethernet vs coax.  Has ANYONE resolved this yet?

Thanks

0 Likes